消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室外消防栓管网有漏点,日常没有压力,不保压,符合法律法规要求吗

室外消防栓管网有漏点,日常没有压力,不保压,符合法律法规要求吗

凡爸 | 2021-05-31 16:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

刘丽波 2021-05-31 22:33 00 [回复]举报

室外消火栓管网有漏点,不保压,时间长了水没有了,就变为干式系统了。不满足《消水规》7.1.1条,室外消火栓系统应为湿式系统。应设稳压设备,维持管网为湿式系统。

凡爸   回复: 刘丽波2021-06-06 22:54

谢谢老师

0    0 [回复]举报

陈小雨 2021-05-31 23:22 00 [回复]举报

不符合,室外消火栓自地面算起动压不低于0.1Mpa,查gb50974

凡爸   回复: 陈小雨2021-06-06 22:53

你说的是7.2.8规定,是市政消火栓。如果我说的系统是消防水池的,7.3中没有提到压力,要求也一样吗?

0    0 [回复]举报

关闭

关闭

手机APP下载