哪些场所需要设置避难走道

一个剧场(开心麻花),设置在二类高层公共建设的5层,5层建筑面积1100平米(4个厅,每个厅100-150平米左右,在大厅的等候区也设置了一个剧场,大厅面积500平米左右)

1.问疏散走道需要设置成避难走道吗?都哪些场所需要设置避难走道?依据什么规范?

2.墙面和地面使用B1材料装修是否可以?

一红到底 | 2024-09-25 15:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2024-09-25 15:59 00 [回复]举报

条文说明:

  避难走道主要用于解决大型建筑中疏散距离过长,或难以按照规范要求设置直通室外的安全出口等问题。避难走道和防烟楼梯间的作用类似,疏散时人员只要进入避难走道,就可视为进入相对安全的区域。为确保人员疏散的安全,当避难走道服务于多个防火分区时,规定避难走道直通地面的出口不少于2个,并设置在不同的方向;当避难走道只与一个防火分区相连时,直通地面的出口虽然不强制要求设置2个,但有条件时应尽量在不同方向设置出口。避难走道的宽度要求,参见本条下沉式广场的有关说明。


建筑设计防火规范 GB50016-2014(2018年版)

6.4.14 避难走道的设置应符合下列规定:    

1 避难走道防火隔墙的耐火极限不应低于3.00h,楼板的耐火极限不应低于1.50h。    

2 避难走道直通地面的出口不应少于2个,并应设置在不同方向;当避难走道仅与一个防火分区相通且该防火分区至少有1个直通室外的安全出口时,可设置1个直通地面的出口。任一防火分区通向避难走道的门至该避难走道最近直通地面的出口的距离不应大于60m。    

3 避难走道的净宽度不应小于任一防火分区通向该避难走道的设计疏散总净宽度。    

4 避难走道内部装修材料的燃烧性能应为A级。    

5 防火分区至避难走道入口处应设置防烟前室,前室的使用面积不应小于6.0m²,开向前室的门应采用甲级防火门,前室开向避难走道的门应采用乙级防火门。    

6 避难走道内应设置消火栓、消防应急照明、应急广播和消防专线电话。