消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水泵出水干管安装电接点压力表的问题

请教一下,消防水泵不得自动停泵,那消防水泵出水干管上安装了电接点压力表,那不是到达上限压力后,自动停泵了么?

消防检查 | 2024-08-15 10:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

周家斌 2024-08-15 16:55 00 [回复]举报

不能设置自动停泵,上限点不接线就是,控制稳压泵的电接点压力表是可以的,

消防检查   回复: 周家斌2024-08-16 09:05

谢谢。

0    0 [回复]举报

阿宸宸宸宸OK 2024-08-15 17:06 10 [回复]举报

个人认为,电接点压力表与压力开关是两回事,规范要求的是安装压力开关,所以我认为安装电接点压力表本身就是错误的,就不要纠结自动停泵的问题了。直接换成电子式的压力开关问题就解决了

消防检查   回复: 阿宸宸宸宸OK2024-08-16 09:09

关键是规范上允许消防水泵设置电接点压力表。

消水规11.0.4 条文说明:为此本次规范制订时规定采用压力开关和流量开关作为水泵启泵的信号。压力开关一般可采用电接点压力表、压力传感器等。

那就压力上限不接线吧,可启不可停。

0    0 [回复]举报

阿宸宸宸宸OK   回复: 消防检查2024-08-16 18:09

感谢,更正了我对压力开关的理解

0    0 [回复]举报

布泽德 2024-08-17 09:53 00 [回复]举报

电接点压力表 只接压降导通那两条线就好了。

南明离火 2024-08-17 12:28 00 [回复]举报

要么不接线,要么 直接上限设置一个 无法达到的压力

关闭

关闭

手机APP下载