消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水池连续补水的疑问

各位

消防水池设有一路补水,消防水池的容积满足火灾延续时间内的用水量,补水时间也是满足要求。

那么,此时一路补水满足法规要求么,是否需要设施二路补水呢?

消防大白菜 | 2024-08-05 16:28
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

西湾子消防小能手 2024-08-06 09:35 00 [回复]举报

《消防给水及消火栓系统技术规范》GB50974-2014 -4.3.5火灾时消防水池连续补水应符合下列规定:

    1、消防水池应采用两路消防给水

周家斌 2024-08-06 11:01 10 [回复]举报

不需要,这和4.3.5条不是一回事,

关闭

关闭

手机APP下载