消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

燃气导热油炉房火灾危险类别是什么?

1、燃气导热油炉房火灾危险类别是乙类、丙类还丁类?

2、采用导热油加热的设施(如果被加热物料是丙类),导热油操作温度超过其闪点,按《石化规》应该为乙类,那么导热油加热的设施就按乙类吗?是否还要上防爆电气?

lxfziyou | 2024-07-26 11:41
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

蘇瑾 2024-12-21 10:46 00 [回复]举报

丁类。

①燃气导热油炉属于锅炉。TSG11-2020

②锅炉房的火灾危险性类别GB50016 条文说明

③有关安全要求

GB 51283 -2020:

5.4.1 燃油、燃气导热油炉房应独立设置,且应布置于有可燃气体、液化烃和甲、乙类设备的全年最小频率风向的下风侧。当工艺要求与甲、乙类的厂房贴邻布置时,应符合下列规定:

1 导热油炉房应采用防火墙分隔;

2 导热油炉房的门和窗、排气筒应位于爆炸危险区域以外;

3 燃气导热油炉房应设置可燃气体报警仪。

5.4.2 导热油炉及附属导热油储罐、导热油炉输送泵等设备周围,应设置防止导热油外溢的措施。

5.4.3 导热油炉系统应安装安全泄放装置。

5.4.4 导热油炉加热燃料气管道应采取下列保护措施:

1 设置低压报警和低低压联锁切断系统;

2 在燃料气调节阀与导热油炉之间设置阻火器。

5.4.5 导热油炉尚应符合现行行业标准《导热油加热炉系统规范》SY/T 0524的规定。

关闭

关闭

手机APP下载