高层内增设上下连通的敞开楼梯

一类高层建筑在装修改造时,建筑内上下层增设上下连通的敞开楼梯(不做疏散使用),上层楼梯洞口周围采用耐火极限不低于3.0h的防火卷帘与其他部分分隔,请问这样是否可以。

烟柱 | 2024-07-15 10:47
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

LHH2737 2024-07-15 13:41 00 [回复]举报

可以,这种做法就类似商场里的自动扶梯

li里 2024-07-15 15:13 00 [回复]举报

楼板新开洞面积小,贯穿楼层小于3层,通常不能当作中庭,不能全部用防火卷帘封闭,应该按《建规》6.5.3条设置防火卷帘。

缱绻一夏 2024-07-15 16:40 00 [回复]举报

可以的,上层三小时防火卷帘,下层挡烟垂壁