消防软管卷盘间距是多少?

只设置消防软管卷盘的场所(如丁戊类厂房),消防软管卷盘的布置间距是多少呢,之前都是按照30米保护半径考虑,这样最远间隔60米,现在看到《建筑设计防火规范》8.2.4条,说布置间距不应大于30米,这样数量就多了,消防软管卷盘的布置间距到底是多少,求教。

开着拖拉机 | 2024-06-21 17:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

黄-江西省景德镇市 2024-06-23 22:57 00 [回复]举报

消防软管卷盘和轻便消防水龙应执行《消防给水及消火栓系统技术规范》GB50974-2014

7.4.6 室内消火栓的布置应满足同一平面有2支消防水枪的2股充实水柱同时达到任何部位的要求,但建筑高度小于或等于24.0m 且体积小于或等于5000m3的多层仓库、建筑高度小于或等于54m且每单元设置一部疏散楼梯的住宅,以及本规范表3.5.2中规定可采用1支消防水枪的场所,可采用1支消防水枪的1股充实水柱到达室内任何部位。

7.4.10 室内消火栓宜按直线距离计算其布置间距,并应符合下列规定:
1 消火栓按2支消防水枪的2股充实水柱布置的建筑物,消火栓的布置间距不应大于30.0m。

一路同行 2024-06-24 08:30 00 [回复]举报

规范特指老年人建筑(个人理解规范)

最帅游客 2024-06-24 10:27 10 [回复]举报

应该是本来要设置室内消火栓,但因火灾危险性不大,考虑到经济因素,所以允许只设置软管卷盘或者轻便水龙,所以布置间距应按同时使用水枪数来决定,两支30米,一只50米。水枪数根据表3.5.2 建筑物室内消火栓设计流量,但不应折减。

香.香 2024-06-24 13:27 00 [回复]举报

丁戊类厂房同一平面保证2枪两股充实水柱,间距不大于30米。室内消火栓两者间考虑间距满足要求,没有保护半径大的说法,只有室外栓才说半径