消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

高位消防水箱问题

2000平的2层单体建筑,使用性质为洗浴,可不可以不设置高位消防水箱?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 10

安洪全 2024-06-07 09:38 00 [回复]举报

 消防设施通用规范 GB55036-2022 

3.0.9 高层民用建筑、3层及以上单体总建筑面积大于10000m²的其他公共建筑,当室内采用临时高压消防给水系统时,应设置高位消防水箱。

喜欢晴天 2024-06-07 09:54 00 [回复]举报

自动喷水灭火系统设计规范 GB50084-2017

10.3.1 采用临时高压给水系统的自动喷水灭火系统,应设高位消防水箱。自动喷水灭火系统可与消火栓系统合用高位消防水箱,其设置应符合现行国家标准《消防给水及消火栓系统技术规范》GB 50974的要求。

消防网友68723 2024-06-07 10:16 00 [回复]举报

是否有其他灭火系统?市政供水能否满足消防系统用水要求?

黄-江西省景德镇市 2024-06-07 11:45 00 [回复]举报

2层单体建筑属于多层建筑,只要任意一层建筑面积不超过1500m²,总建筑面积不超过3000m²就不需要设喷淋,通常这类建筑高度不可能超过15米,体积肯定超过5000m³,那么室内消火栓是必须设置的,室内消火栓流量不低于15L/s,通常市政供水压力为0.25MPa(以现场实际条件为准),能够满足此建筑最不利点静压≥0.07MPa,室内消火栓的水源可以直接接入市政给水管。

若该建筑附近市政供水压力满足不了室内消火栓最低静压,就得考虑在接市政供水的给水管上增加稳压设施(平时稳压)和加压消火栓泵(火灾时加压给水)。只设置高位消防水箱并不能满足火灾持续时间2小时和室内消火栓流量的要求,通常这类建筑建造时不会考虑屋面过大的承载力,那么建筑结构是否能够承载十几二十吨高位水箱重量就必须严肃考虑,以免造成安全隐患。

易谁寒 2024-06-07 14:31 00 [回复]举报

不超过2层不需要设

消防网友74993 2024-06-07 14:43 00 [回复]举报

压力满足的前提下,可以不用设

倜圳 2024-06-07 15:31 00 [回复]举报

要做的吧

阳明心 2024-06-07 15:39 00 [回复]举报

如果市政水的压力能满足最不利点的压力要求,可以不设的

我头发贼黑 2024-06-07 16:08 00 [回复]举报

6.1.9 室内采用临时高压消防给水系统时,高位消防水箱的设置应符合下列规定:     1 高层民用建筑、总建筑面积大于10000㎡且层数超过2层的公共建筑和其他重要建筑,必须设置高位消防水箱;

老刘头 2024-06-08 16:24 00 [回复]举报

一般情况下,设计会给个高位水箱。如果是改造工程考虑结构问题,可以不设,但会考虑消防供水的稳定性设置稳压系统。也可以考虑和附近建筑共用消防水源,单体建筑周围啥都没有?不可能吧

关闭

关闭

手机APP下载