关于应急疏散标志灯规格的选择问题。

请问疏散标志灯大小规格的选择是根据场所的室内高度还是标志灯的设置高度来定?比如,室内高度4.6m,但疏散指示灯安装在墙上1m以下,安全出口指示灯安装在2.4m,需要选择大型或者特大型标志灯吗?

GermanLee | 2024-05-27 11:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

倜圳 2024-05-27 13:38 00 [回复]举报

按建筑层高

高山流水2024 2024-05-27 14:22 10 [回复]举报

6 标志灯的规格应符合下列规定:
      1)室内高度大于4.5m的场所,应选择特大型或大型标志灯;
      2)室内高度为3.5m~4.5m的场所,应选择大型或中型标志灯;
      3)室内高度小于3.5m的场所,应选择中型或小型标志灯。

消防应急照明和疏散指示系统技术标准 GB51309-2018 >

消防网友55731 2024-05-27 16:21 20 [回复]举报

此条特指高位吊挂式指示灯具,其他灯具不受此限。

消防检查   回复: 消防网友557312024-05-28 09:23

请教下,哪里的条文特指悬挂式。

0    0 [回复]举报

潘天坤 2024-06-03 16:03 01 [回复]举报

1、《消防应急照明和疏散指示系统技术标准》(GB51309-2018)规范正文描述为“室内高度”,条文说明描述为“设置高度”,正文和条文说明存在矛盾,造成大家尺度不好统一。PS:其实正文效力是大于条文说明的,但是条文说明也确实提到了,按正文从严要求,会存在些许争议。
2、有多个省份的技术文件明确“根据安装高度选择标志灯具规格尺寸”。
3、根据“室内高度”还是“设置高度”选择标志灯具的规格尺寸,可以先参照本区域内技术文件,如果区域内有技术文件要求的,按照技术文件要求执行,如果没有区域技术文件要求的可以上文件让设计明确选择依据。也可以跟本区域相关技术人员讨论咨询,可能很多专家的理解不一致。
4、个人认为:如果区域内技术文件没有相关规定,按照规范正文要求“按照室内高度选择”是可以的。但是因为条文说明的存在,可能会存在争议。
目前小潘是按照安装高度来把控(没有区域技术文件,行业内理解不统一),规范存在争议点,从严落实容易造成社会矛盾,个人觉得自己这个做法是一种无奈的妥协。