消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

老年人照料设施是多个独立的单层建筑,每个独立的建筑15张床位,请问需不需要设置自动喷水和自动报警系统?它这种是按照独立的建筑还是按照总体界定?

老年人照料设施是多个独立的单层建筑,每个独立的建筑15张床位,请问需不需要设置自动喷水和自动报警系统?它这种是按照独立的建筑还是按照总体界定?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

皮特拖 2024-04-08 12:11 00 [回复]举报

根据规范要求老年人照料设施要设自喷和和自报

阳明心 2024-04-08 16:52 00 [回复]举报

根据《建筑防火通用规范》GB 55037-2022,第8.1.9.6条需要设

同同不同 2024-04-09 07:32 00 [回复]举报

老照设施不论面积层数都得设置自喷系统、火报系统

若风12333 2024-04-10 13:19 10 [回复]举报

个人认为您所说的不属于老年照料设施,根据《建筑设计防火规范 GB50016-2014(2018年版)》5.1.1条文说明本规范条文中的“老年人照料设施”是指现行行业标准《老年人照料设施建筑设计标准》JGJ 450—2018中床位总数(可容纳老年人总数)大于或等于20床(人),为老年人提供集中照料服务的公共建筑,包括老年人全日照料设施和老年人日间照料设施。根据您所描述多个单体建筑,且每个15人,每个建筑人数不超过20人,不符合老年人照料设施的定义。个人认为不应按总体人数判断,应按照单体所能容纳的人数来判断。根据《老年人照料设施建筑设计标准 JGJ450-2018》1.0.2 本标准适用于新建、改建和扩建的设计总床位数或老年人总数不少于20床(人)的老年人照料设施建筑设计。也可进行判断。不属于老年人照料设施自然也就不需要设置自喷和自报。(个人观点,仅供参考)

阳明心   回复: 若风123332024-04-11 16:43

看得仔细,有道理,按照这个还真的不用设自喷。

0    0 [回复]举报

南明离火 2024-04-12 14:04 00 [回复]举报

不用 每栋面积都很小已经  物理上限制了 火灾载荷 和 规模

关闭

关闭

手机APP下载