二氧化碳灭火器称重频率

二氧化碳灭火器称重频率

爱好学习 | 2024-04-02 10:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

灭邪斩 2024-05-02 16:50 11 [回复]举报

根据建筑灭火器配置验收及检查规范 GB50444-2008规定

5.2.1 灭火器的配置、外观等应按附录C的要求每月进行一次检查。
5.2.2 下列场所配置的灭火器,应按附录C的要求每半月进行一次检查。
    1 候车(机、船)室、歌舞娱乐放映游艺等人员密集的公共场所;
    2 堆场、罐区、石油化工装置区、加油站、锅炉房、地下室等场所。