消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟量计算

请问一个地上公共建筑区域450平米,划分多个房间,其中大于100平米的设计了机械排烟,其他都是小于50平米的无窗房间,机械排烟量计算时需包括无窗房间面积嘛?

消防网友9144 | 2021-02-22 11:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

牛疼 2021-02-23 15:32 00 [回复]举报

无需计算

米米果果 2022-12-16 15:56 00 [回复]举报

若所有无窗房间的总面积大于200平米,则需要设置排烟设施,排烟口可设置在走道。

李勤 2025-07-03 17:09 00 [回复]举报

无窗房间小于50平米房间内不需要,但是设置走道排烟时需要考虑在内。

潘天坤 2025-07-04 14:02 00 [回复]举报

无可开启外窗的房间区域的总建筑面积大于200平方米时,应考虑区域设置排烟设施,此情况可以在走道设施机械排烟,一般可以按不低于13000考虑走道排烟量,有些地区考虑走道排烟量的时候会额外加上一间最大建筑面积的功能房间


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准





关闭

关闭

手机APP下载