消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

1、楼梯间消火栓明装是否违反建规6.4.1-3楼梯间内不应有影响疏散的凸出物或其他障碍物?

2、封闭楼梯间是窗户自然排烟,但是楼梯平台处的外窗是内开,是否算影响疏散?有明确具体的规范条文?

psyfss | 2024-02-05 20:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

安洪全 2024-02-06 10:02 00 [回复]举报

1、消火栓明装没问题,问题是明装后影不影响最小疏散净宽度,如果影响就不行;

2、内开可以,完全打开后影响最小疏散净宽的,就算影响疏散。

周家斌 2024-02-06 13:45 00 [回复]举报

不影响疏散净宽和高度的情况下,是不算障碍物的。


我是小鱼鱼 2024-02-06 14:22 00 [回复]举报

1.如果不在半径内,不算障碍物。

2.内平开如果高度在2米内,算障碍物。


喜欢晴天 2024-02-06 15:34 00 [回复]举报

建规6.4.1条第3款的条文说明是这么描述的“人员在紧急疏散时容易在楼梯出入口及楼梯间内发生拥挤现象,楼梯间的设计要尽量减少布置凸出墙体的物体,以保证不会减少楼梯间的有效疏散宽度。”

所以在保证楼梯间疏散净宽度的前提下,室内消火栓箱可以明装,不违规。

瞎飞 2024-02-07 15:32 00 [回复]举报

封闭楼梯间不允许室内消火栓,普通楼梯间可以

张冬华 2024-02-12 20:53 00 [回复]举报

我认为不算!楼梯间消火栓是设置在梯段处的话,就算!平台上不会影响实际疏散宽度

关闭

关闭

手机APP下载