气体灭火防护区面积问题:当防护区面积大于800平方米或者体积大于3600立方米时,气体灭火系统该怎么设置?

当防护区面积大于800平方米或者体积大于3600立方米时,气体灭火系统该怎么设置?

消防设计42 | 2024-01-18 19:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

AI老倪 2024-01-19 09:27 00 [回复]举报

一般不要突破哈,超太多就得做物理分隔。

细水雾-气体灭火-消防性能化-磐龙 2024-01-22 15:20 00 [回复]举报

3.2.4 防护区划分应符合下列规定:
    1 防护区宜以单个封闭空间划分;同一区间的吊顶层和地板下需同时保护时,可合为一个防护区;
    2 采用管网灭火系统时,一个防护区的面积不宜大于800m²,且容积不宜大于3600m³;
    3 采用预制灭火系统时,一个防护区的面积不宜大于500m²,且容积不宜大于1600m³。