消防取水口取水深度是否需要考虑海拔影响?

对于消防车取水高度的要求,高海拔地区是否需要考虑海拔影响?若需考虑,怎么计算取水高度?

尔东 | 2024-01-16 14:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防资源网 2024-01-16 16:44 20 [回复]举报


消防水池取水口设计-若干问题详解https://b.1190119.com/m/article-7411.htm

消防网友32804 2024-01-17 11:29 10 [回复]举报

消防车的取水高度,与大气压、最高环境温度下的饱和蒸气压、必须汽蚀余量、管路损失等相关,通常情况下消防车的取水高度计算如下:

1.大气压力不小于10m水柱的地区,最大吸水高度可按6m取值。

2.大气压力小于10m的地区,最大吸水高度为大气压(m水柱)-4m确定。