消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

二氧化碳灭火系统

二氧化碳灭火系统已知防护区的尺寸大小,危险等级,预布置时如何确定喷头个数进行管网布置

why | 2021-01-25 09:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

黄辉 2021-01-25 12:09 00 [回复]举报

二氧化碳灭火系统没有给出喷头的间距规定,建议参考气体灭火系统设计规范 GB50370-2005 


3.1.12 喷头的保护高度和保护半径,应符合下列规定:
      1 最大保护高度不宜大于6.5m;
      2 最小保护高度不应小于0.3 m;
      3 喷头安装高度小于1.5 m时,保护半径不宜大于4.5 m;
      4 喷头安装高度不小于1.5m时,保护半径不应大于7.5 m。

why   回复: 黄辉2021-01-25 13:22

意思是根据保护半径计算出保护面积,而后确定喷头个数吗

0    0 [回复]举报

黄辉   回复: why2021-01-26 10:19

是的。

一般来说,建议采用专用的设计软件设计,软件会根据防护区的尺寸,自动布置喷头。会根据管网的要计算结果,确定喷头的型号等。

0    0 [回复]举报

why   回复: 黄辉2021-01-26 14:01

谢谢,能介绍一款专用软件吗

0    0 [回复]举报

黄辉   回复: why2021-01-27 09:29

天津兆龙。软件有点小贵。

4    0 [回复]举报

关闭

关闭

手机APP下载