楼梯间直通屋面的出口可否不设门?

    本网站中,消防专题→消防问答


    请教一下,上文“普通门”是什么概念?当满足自然通风条件的封闭楼梯间或防烟楼梯间,最高处直通屋面的出口,可否不设门?或者,可否设置为向外开启的栅栏式的平开门(可通风防盗)。

    提出这个问题是基于:《建筑防烟排烟系统技术标准》( GB 51251-2017)3.2.1 采用自然通风方式的封闭楼梯间、防烟楼梯间,应在最高部位设置面积不小于1.0㎡的可开启外窗或开口,及3.2.1条文说明“ 一旦有烟气进入楼梯间如不能及时排出,将会给上部人员疏散和消防扑救进攻带来很大的危险。根据烟气流动规律在顶层楼梯间设置一定面积的可开启外窗可防止烟气的积聚,以保证楼梯间有较好的疏散和救援条件。”  若是基于这个思路,楼梯间直通屋面的出口不设门的话,可否作为GB 51251 3.2.1所提到的开口?

     为什么?谢谢。

石头1190 | 2023-12-20 15:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-12-20 17:10 20 [回复]举报

消防概念中的“普通门”就是不具备防火防烟功能的门


个人认为可以代替,理由:虽然形式不同,但能达到相同的功能

dl那片海 2024-07-16 08:54 00 [回复]举报

如果楼梯是封闭楼梯间或防烟楼梯间屋面出口就必须设门,而且是与下面楼梯间一样的门