娱乐场所两个疏散门:一个为安全出口,一个为室内疏散门场地疏散距离怎么算,按多少米

娱乐场所两个疏散门一个为室外安全出口,一个为室内疏散门室内的疏散距离怎么算

娜娜老公 | 2023-11-21 16:28
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

阳明心 2023-11-21 16:44 00 [回复]举报

我的是昵称 2023-11-22 08:24 10 [回复]举报

室内到疏散门,一二级建筑按9米算,有自动灭火系统加25%为11.25m.

袋形走道尽端或两侧是室门,到安全出口也是9m,有自动灭火的加25%,也是11.25m.

娜娜老公   回复: 我的是昵称2023-11-22 11:17

您好老师 天津回复深圳消防《关于歌舞娱乐放映游艺场所疏散距离有关问题的复函》时说的疏散门为安全出口时,可以按照18米。是否可以往室内疏散门疏散的按9米,往室外安全出口方向疏散的按18米呢

0    0 [回复]举报

我的是昵称   回复: 娜娜老公2023-11-22 14:00

不是,他说的18米,是内9米,加外9米,一共18米。有的图纸的疏散距离是室内的距离加室外安全出口的,也就是说,你室内的疏散距离是5米,那外面是13米,也可以解释的通。

1    0 [回复]举报

娜娜老公   回复: 我的是昵称2023-11-22 14:44

好的 谢谢

0    0 [回复]举报

平心 2023-11-22 20:53 00 [回复]举报

你好老师,请问一下我可以在哪个规范里找到你所说的“室内疏散门场地疏散距离”的定义呢,谢谢

娜娜老公   回复: 平心2023-11-24 15:44

《建筑防火规范GB50016-2014(2018年版)》5.5.17可以看到

0    0 [回复]举报

平心   回复: 娜娜老公2023-11-24 20:21

谢谢

0    0 [回复]举报