消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

住宅小区的10KV供配电房内需不需配制气体灭火系统


住宅小区内的专用供配电房属于物业管理,房间内只配制了干粉灭火器,需不需要配制预制式气体灭火系统?

消防网友69065 | 2023-10-12 09:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

周家斌 2023-10-12 17:18 00 [回复]举报

不是必须的。

潘天坤 2024-06-29 23:30 00 [回复]举报

是独立建造的配电室,还是附属在高层民用建筑内的配电室呢

一般认为高层民用建筑的配电室属于特殊重要设备室,应设置自动灭火系统,并宜采用气体灭火系统

其他建筑的配电室可以参照执行,不做强制要求,不过有时候设计单位认为一些区域比较重要也会设置自动灭火系统

建规GB50016条文说明提及:高层民用建筑内火灾危险性大,发生火灾后对生产、生活产生严重影响的配电室等,也属于特殊重要设备室

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载