消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消火栓和自动喷水灭火系统

电接点压力表可以作为稳压泵控制方式,能不能作为消火栓泵和喷淋泵的启动方式。有没有规范说明?

李秀举 | 2023-10-06 20:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2023-10-07 08:37 10 [回复]举报

可以的,但是要泵启动后自锁。不要自动停泵

安洪全 2023-10-07 09:05 10 [回复]举报

首先,“自动喷水灭火系统设计规范 GB50084-2017”中明确了启泵的方式:


11.0.1 湿式系统、干式系统应由消防水泵出水干管上设置的压力开关、高位消防水箱出水管上的流量开关和报警阀组压力开关直接自动启动消防水泵。


湿式系统、干式系统消防泵的自动启动应由报警阀组的压力开关、出水干管的压力开关、高位消防水箱的流量开关启动,其他的方法不可靠也不在规范的约定范围之内,没有依据。


其次,稳压泵的设置目的并不是启动消防泵,只是其原理上与启泵的原理有一致性,但是可能会导致误启泵,既然规范给出了明确的操作与控制方法,要规范要求执行即可,既可以规避误启动的情况,也有执行依据。

我的是昵称 2023-10-07 09:38 10 [回复]举报

规范上没有明确说明,只说了三种直接启泵的控制方式,高位消防水箱流量开关,出水干管低压压力开关,报警阀压力开关。但在以往消防设施检测过程中,是有利用电接点压力表代替出水干管低压压力开关的事例。不过,出现这种事例的往往是老的小区或设施。如果你的是老设备就按以往的检测维保就行,毕竟以前是通过验收了的。如果是新的建筑,那还是老实的用压力开关吧。用电接点估计验收不过。我们这是法无授权不可行的行业。严谨些没错事。

郝琦 2024-03-17 11:46 00 [回复]举报

图集表示可以

关闭

关闭

手机APP下载