排烟量计算问题

一般按照面积乘以60 走道13000房间15000 

可是规范每个防烟分区排烟量V = MρT / ρ0T0            (4.6.13-1)
T =T0 + △T          (4.6.13-2)
式中:V——排烟量(m³/s);
         ρ0——环境温度下的气体密度(kg/m³),通常T0=293.15K,ρ0=1.2(kg/ m³);
        T0——环境的绝对温度(K);
        T——烟层的平均绝对温度(K)。

需要这么计算吗

艾zz | 2023-08-31 16:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

张治福 2023-09-01 13:45 00 [回复]举报

我是搭车来学习的。

潘天坤 2024-06-20 00:50 00 [回复]举报

空间净高大于6米的场所,需要通过计算确定,且不应小于表4.6.3中的数值

楼主发的公式就是计算之一的数据