Co2气体灭火的瓶组问题

请问驱动瓶组是否有规格型号一致的瓶组设置条件?

| 2023-08-30 14:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

张牙舞爪的张 2023-08-30 15:07 00 [回复]举报

驱动气体瓶组误差不大于10mm

  回复: 张牙舞爪的张2023-08-30 15:13

您说的这是设置高度,我想问的是驱动瓶组间存在大小瓶的问题

0    0 [回复]举报

黄辉   回复: 2024-01-12 08:49

张坤鹏 张总的回答,实际上已经明确了,一套组合分配系统的驱动气体瓶组的规格型号应一致。不可有大小瓶的情况。


即使是某防护区使用的灭火剂瓶组少,可用小的驱动瓶,某防护区使用灭火剂瓶组数量多,要用大的驱动瓶。按驱动气体瓶组误差不大于10mm的要求,也需要统一使用大驱动瓶。

0    0 [回复]举报