地下1000平的超市,和地上1000平的独立超市,二层1062平的独立餐馆,要不要设室内消火栓

久久 | 2023-07-25 17:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-07-25 17:30 00 [回复]举报

大概率要设,涉及建筑体积未知,您可以自行核对。


建筑防火通用规范 GB55037-2022

8.1.7 除不适合用水保护或灭火的场所、远离城镇且无人值守的独立建筑、散装粮食仓库、金库可不设置室内消火栓系统外,下列建筑应设置室内消火栓系统:    

1 建筑占地面积大于300㎡的甲、乙、丙类厂房;    

2 建筑占地面积大于300㎡的甲、乙、丙类仓库;    

3 高层公共建筑,建筑高度大于21m的住宅建筑;    

4 特等和甲等剧场,座位数大于800个的乙等剧场,座位数大于800个的电影院,座位数大于1200个的礼堂,座位数大于1200个的体育馆等建筑;    

5 建筑体积大于5000m³的下列单、多层建筑:车站、码头、机场的候车(船、机)建筑,展览、商店、旅馆和医疗建筑,老年人照料设施,档案馆,图书馆;   

6 建筑高度大于15m或建筑体积大于10000m³的办公建筑、教学建筑及其他单、多层民用建筑;    

7 建筑面积大于300㎡的汽车库和修车库;    

8 建筑面积大于300㎡且平时使用的人民防空工程;    

9 地铁工程中的地下区间、控制中心、车站及长度大于30m的人行通道,车辆基地内建筑面积大于300㎡的建筑;   

10 通行机动车的一、二、三类城市交通隧道。

周家斌 2023-07-26 09:57 00 [回复]举报

按照描述可以判断要设置的。

二公子二公子 2023-07-26 16:20 00 [回复]举报

建筑体积超过5000m³,必须设置