消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

应急排烟设施设置问题

规范要求是无可开启外窗的建筑或部位设应急排烟设施,如果一层丙类仓库面积4000平方仅仅做了一个平方的可开启外窗就不用做应急排烟设施了么?

紫星梦宸 | 2023-07-04 10:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

安洪全 2023-07-04 11:23 20 [回复]举报

我理解的“2.2.5”的条款主要的设置目的在于“救援设施”,为了便于救援,强调设置可以“开启的应急”排烟窗,与防排烟系统的设置目的有别,如果设置的应急排烟窗兼顾“防排烟”的功能,当然还要满足防排烟系统里面具体的细则。

现在“火通”里面没说清楚,主要是在各规范尚未跟进更新,将来各系统专业规范更新后应该会有细则出台。


同同不同   回复: 安洪全2023-07-04 12:56

应是为了救援用,在消防救援时应急排掉部分烟热,满足救援人员进入的温度及清晰度,并不意味着这应急排烟排热窗口就能满足防排烟要求,仍应参照火通规、消通规及烟规

1    0 [回复]举报

安洪全   回复: 同同不同2023-07-04 13:38

感谢分享

0    0 [回复]举报

紫星梦宸   回复: 同同不同2023-07-04 14:10

目前各还没有同步更新的情况下,这一类的项目怎么做呢?这个可开启外窗满足什么情况不需要做应急排烟设施?

0    0 [回复]举报

安洪全   回复: 紫星梦宸2023-07-04 14:21

相对于应急救援窗,防排烟系统的检查会更严格,这两者之间没有替代关系,达到了设置条件就各设各的,即使有覆盖的关系,也应该是设置了防排烟可以在应急排烟窗上做出让步。

0    0 [回复]举报

关闭

关闭

手机APP下载