消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

火灾时不应立即切掉的非消防电源,要多久才能切掉?

 

对于在火灾时不应立即切掉的非消防电源(如正常照明、生活给水泵和客梯等),那要多久后才能切掉?

与笑同行 | 2023-06-19 15:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2023-06-19 15:44 00 [回复]举报

当需要切断正常照明时,宜在自动喷淋系统、消火栓系统动作前切断。


火灾自动报警系统设计规范 GB50116-2013

4.10.1 消防联动控制器应具有切断火灾区域及相关区域的非消防电源的功能,当需要切断正常照明时,宜在自动喷淋系统、消火栓系统动作前切断。


4.20.2 的条文说明:

火灾确认后,火灾自动报警系统是否应切断火灾区域及相关区域的非消防电源,在国内是极具争议的问题,各地区、各设计院的设计差异很大。理论上讲,只要能确认不是供电线路发生的火灾,都可以先不切断电源,尤其是正常照明电源,如果发生火灾时正常照明正处于点亮状态,则应予以保持,因为正常照明的照度较高,有利于人员的疏散。正常照明、生活水泵供电等非消防电源只要在水系统动作前切断,就不会引起触电事故及二次灾害。其他在发生火灾时没必要继续工作的电源或切断后也不会带来损失的非消防电源,可以在确认火灾后立即切断。火灾时应切断的非消防电源用电设备和不应切断的非消防电源用电设备如下:    

(1) 火灾时可立即切断的非消防电源有:普通动力负荷、自动扶梯、排污泵、空调用电、康乐设施、厨房设施等。    

(2) 火灾时不应立即切掉的非消防电源有:正常照明、生活给水泵、安全防范系统设施、地下室排水泵、客梯和Ⅰ~Ⅲ类汽车库作为车辆疏散口的提升机。    

(3) 关于切断点的位置,原则上应在变电所切断比较安全。当用电设备采用封闭母线供电时,可在楼层配电小间切断。

关闭

关闭

手机APP下载