自带蓄电池的消防应急灯具所接的配电箱还需要接发电机电源及安装双切开关吗(二级负荷)

自带蓄电池的消防应急灯具所接的配电箱还需要接发电机电源及安装双切开关吗(二级负荷)

小曾 | 2023-05-15 11:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

无名之辈 2023-05-16 10:27 00 [回复]举报

      集中控制型系统,应急照明配电箱应由所在防火分区(楼层)的消防电源供电,除三级负荷无需双回路供电外,特级一级二级均需双回路供电,消防配电箱内安装自动转换开关,实现消防主备电自动切换功能;

      非集中控制型系统,应急照明配电箱可由正常照明配电箱供电,不涉及到双回路的问题。

小曾   回复: 无名之辈2023-06-12 10:00

好的,谢谢

0    0 [回复]举报