消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

系统压力及稳压泵启动问题

问题1:系统水压降了,稳压泵无法自动启泵,可以手动启动稳压泵,手自动状态正确。同样的情况一起可以自动启动现在不可以了,可能是什么原因?

问题2:管路的水压(压力表)经常降压是怎么回事哩?、?系统水压为什么会降低,“高位水箱的液位计并没有降低”

流苏 | 2023-04-19 09:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

caiyw 2023-04-19 10:11 00 [回复]举报

1、稳压泵不能自动,检查启泵压力值设置是否正确以及电接点压力表或压力变送器是否完好;

2、系统水压不稳定一般是系统管路漏水(管道泄漏、止回阀关闭不严、人为放水等),

卡卡阿卡 2024-01-19 15:37 00 [回复]举报

1、先看看稳压泵控制柜的线路和器件的设置情况是否有问题?如果没问题的话,调整电接点压力表的启动下限,看看能不能启泵,调整电接点压力表的停止上限看看能不能停泵。判断电接点压力表的设置和其工作状态,通常比较常见的是电接点压力表上下限设置有问题或者电接点压力表损坏。

2、管路降压通常是系统存在泄漏,一般可分为外部的泄漏和系统内部的泄漏,要具体情况具体分析。高位水箱液位不降是因为高位水箱的补水是一直开着的,通过浮球阀控制高位水箱的液位。

关闭

关闭

手机APP下载