消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

电气照明线路用线规格有规范吗?

电气照明线路用线规格有规范吗?查了一下规范,还真没要求照明线路必须用2.5平方的。

沝奀 | 2023-03-22 10:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

明亮晶莹 2023-03-22 11:18 10 [回复]举报

GB50259-96  电气装置安装工程电气照明装置施工及验收规范:2.0.2 


照明用线分为民用建筑,工业建筑,  室外


 铝线最低不能低于2.5mm2, 

 铜线分别不低于      0.5mm2, 0.8mm2,1.0mm2, 

 铜芯软线分别不低于0.4mm2,0.5mm2,1.0mm2



关闭

关闭

手机APP下载