二层独立商业安全出口的设置

两层的小商业,每层面积150平米,二层商业可以通过一个一拖二的楼梯疏散到首层吗?

鱼大胖 | 2023-03-21 21:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

aalwbw 2023-03-22 08:55 00 [回复]举报

需要2个安全出口的

明亮晶莹 2023-03-22 11:00 00 [回复]举报

你题目描述的不清楚,你是单独的两层的小商业房还是住宅楼下的商业服务网点,如果是二层的商业服务网点,两层面积小于200平方可以通过一个一拖二的楼梯疏散到首层,但是要保证从二层的任意一点到室内楼梯,经过楼梯到达首层,然后到室外的距离之和符合《建筑设计防火规范》GB50016-2014(2018年版)5.5.17要求。你现在两层的面积加起来300平方,超过了200平方,所以必须设置两个安全出口。

陈曲 2023-03-27 16:45 00 [回复]举报

满足疏散距离的前提下 可以一部楼梯 即任意一点到安全出口距离不大于22米(有自喷时27.5米楼梯按1.5倍投影计算)