一类高层住宅建筑防烟楼梯首层的安全出口前设置了向下的踏步阶梯,是否符合规范要求,是否需要按1.4m内不可设置踏步规范的要求整改?

一类高层住宅建筑防烟楼梯首层的安全出口前设置了向下的踏步阶梯,是否符合规范要求,是否需要按1.4m内不可设置踏步规范的要求整改?

小曾 | 2023-03-15 15:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

张牙舞爪的张 2023-03-15 16:10 00 [回复]举报

那是人密场所才有这项规定。住宅建筑里面没有人密场所,自然就不需要。

小曾   回复: 张牙舞爪的张2023-03-15 17:26

收到,感谢

0    0 [回复]举报

iutopia 2023-03-15 17:08 00 [回复]举报

你是没看到《建规》的条文说明,

5.5.19 观众厅等人员比较集中且数量多的场所,疏散时在门口附近往往会发生拥堵现象,如果设计采用带门槛的疏散门等,紧急情况下人流往外拥挤时很容易被绊倒,影响人员安全疏散,甚至造成伤亡。本条中“人员密集的公共场所”主要指营业厅、观众厅,礼堂、电影院、剧院和体育场馆的观众厅,公共娱乐场所中出入大厅、舞厅,候机(车、船)厅及医院的门诊大厅等面积较大、同一时间聚集人数较多的场所。本条规定的疏散门为进出上述这些场所的门,包括直接对外的安全出口或通向楼梯间的门。     本条规定的紧靠门口内外各1.40m范围内不应设置踏步,主要指正对门的内外1.40m范围,门两侧1.40m范围内尽量不要设置台阶,对于剧场、电影院等的观众厅,尽量采用坡道。


小曾   回复: iutopia2023-03-15 17:27

收到,感谢

0    0 [回复]举报

李勤 2023-03-16 11:39 00 [回复]举报