消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

温度低于4°的北方地区车库预作用系统

北方地区车库冬季通常温度低于4°,适合预作用系统。现无梁楼盖,十字梁(梁格4.2*4.2)很多,采用扩大覆盖面积喷头造价更低。但是《喷规》6.1.1条规定民用建筑采用扩大覆盖面积喷头,应为快速响应型。6.1.7条文解释:快速响应洒水喷头仅用于湿式系统。就限制了扩大覆盖面积喷头在冬季低温地区的使用。单连锁预作用系统,电气探头动作灵敏度高于闭式喷头,喷头动作之前报警阀已经打开,管道充满水,待喷头动作即可喷水灭火。北方低温地区的预作用系统,能否采用扩大覆盖面积喷头,或者扩大覆盖面积喷头标准响应型?

mshm | 2023-02-03 17:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

张牙舞爪的张 2023-02-03 20:21 10 [回复]举报

应该可以吧。毕竟在喷头爆破前管道就已经充满水,可以理解为就是湿式系统了。

一路同行 2023-02-04 11:25 10 [回复]举报

可用,单联锁预作用只是采取了一种更可靠的防冻措施,有报警信号以后系统转为湿式,但是喷头未破裂,这也对应规范要求仅湿式可以用的要求。

仅代表个人关点

刘丽波 2023-02-05 15:09 10 [回复]举报

车库执行喷规6.1.1时,应参考仓库栏,不是民用建筑栏。预作用系统执行6.1.4

mshm   回复: 刘丽波2023-02-08 09:17

刘老师,是不是可以理解为:仓库的闭式系统,仅限使用规范列出的三种喷头,而扩大覆盖面积喷头,不在选用的范围内

0    0 [回复]举报

消防黄河 2023-02-08 08:01 10 [回复]举报

可以。注意您所列举两条规范仅是对湿式系统喷头选择的规定。预作用为干式系统。干式系统喷头选型按6.1.4条执行。

消防黄河 2023-02-08 08:01 10 [回复]举报

可以。注意您所列举两条规范仅是对湿式系统喷头选择的规定。预作用为干式系统。

关闭

关闭

手机APP下载