小型商店的疏散必须要两部楼梯吗?

总层数8层的公寓楼,底部两层划分成小型商业,每个商业一二层总面积300平米左右,都需要设置两部疏散楼梯吗?

刘园园 | 2022-11-18 09:09
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

永锅 2022-11-18 10:44 00 [回复]举报

小型商业的定义是否为商业服务网点,如是疏散楼梯参照建规5.4.11条进行设置,如为商业,二至一层需设两部疏散楼梯。

张牙舞爪的张 2022-11-19 13:52 00 [回复]举报

判定该建筑是住宅建筑还是公共建筑。正常你形容的建筑一般是住宅;可你又说是公寓,又应该属于多功能组合建造的公共建筑。看验收意见书确定后,如果是住宅建筑看《建规》5.4.11,公共建筑看《建规》5.5.8。

刘园园   回复: 张牙舞爪的张2022-11-22 11:45

谢谢您!属于多功能组合建造的公共建筑,套《建规》5.5.8

0    0 [回复]举报