消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防系统供水管道公称压力选择

消防系统计算工作压力为1.5MPa,室外埋地消防给水管道如果选用钢丝网骨架管,其公称压力如何选择?是按工作压力1.5MPa直接选择1.6MPa管道,还是要考虑管道在试压下的试验压力(工作压力×1.5)2.3MPa而选择2.5MPa的管道?

画图匠 | 2022-10-27 11:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

逍遥仙 2022-10-27 12:48 00 [回复]举报

你应该想表达的是设计工作压力1.5Mpa吧,此时系统工作压力为1.2P-1.4P之间即1.8Mpa-2.1Mpa,大于1.6Mpa得用无缝钢管。钢丝网骨塑只适合系统工作压力不大于1.6Mpa(埋地)。系统工作压力大于1Mpa,应取P+0.4即2.2-2.5Mpa取2.5Mpa试压即可

画图匠   回复: 逍遥仙2022-10-27 15:18

不是的。系统工作压力按泵出口1.2~1.4倍加上消防水池到泵出口液位高差计算得到系统工作压力是1.5MPa。采用钢丝网骨架管道时,管网试压按的系统工作压力×1.5试压到2.25MPa,所以我纠结的点在于,消防系统工作压力1.5MPa,我选择1.6MPa的钢丝网骨架管按理说应该是可以的,但是按照规范计算试压要求2.25MPa,超过管道工程压力(1.6MPa),这样可行吗?管道供货商一直说公称压力为1.6MPa的钢丝网骨架管试压时不能超过管道的公称压力。

0    0 [回复]举报

逍遥仙   回复: 画图匠2022-10-27 16:50

平时系统工作也不会超过1.6Mpa就没必要担心,这个强度试验取值没问题,强度试压也就半小时这样就顶不住了就有点说不过去了。什么东西都有余量,总不能到时突然压力波动大于了1.6Mpa一点就突然甭管了吧,更何况工作时达不到这个压力。试压时不能超压就是扯淡,你看消防很多设备试验压力都比工压大,这是正常的。

1    0 [回复]举报

画图匠   回复: 逍遥仙2022-10-27 20:13

感谢解答。我们的观点是一致的。

0    0 [回复]举报

关闭

关闭

手机APP下载