消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

设置气体灭火的防护区,当位于地下或地上无窗或固定窗的房间,应设置通风设施,是否需要在房间内外便于操作处设置排风机启动按钮

设置气体灭火的防护区,当位于地下或地上无窗或固定窗的房间,应设置通风设施,是否需要在房间内外便于操作处设置排风机启动按钮;气体灭火防护区内设置的通风是否属于事故排风

消防砖家 | 2022-10-26 09:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

周家斌 2022-10-26 10:36 00 [回复]举报

需要的,民用建筑供暖通风与空气调节设计规范 GB50736-2012,强条!

潘天坤 2024-06-29 23:26 00 [回复]举报

气体灭火后的机械排风,可以按照民用和工业的通风空调规范事故通风要求及气体灭火规范要求,在室内及室外设置操作开关

气体灭火后的机械排风可以认为是类似事故通风

关闭

关闭

手机APP下载