消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

住宅计量箱消防切电

住宅项目,设计院图纸设计了计量箱消防切电,项目现场计量箱是由供电局提供的,供电局不允许他的箱子内有其他东西,消防切电没法施工,这块该如何处理?

九九 | 2022-08-27 23:28
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

周家斌 2022-08-29 09:08 00 [回复]举报

设计变更取消。

南明离火   回复: 周家斌2022-08-29 17:25

这种设计变更设计估计不肯出吧

0    0 [回复]举报

九九   回复: 周家斌2022-08-29 23:42

设计回复不能取消,也没有提出有效的办法

0    0 [回复]举报

周家斌   回复: 九九2022-09-02 11:43

不是强条,可以的,供电局的供电系统的确是不能随便断电的,规范条文也是有争议的,

0    0 [回复]举报

李勤 2022-08-30 15:00 00 [回复]举报

设计回复,要求变更,要不验收出了问题,说你不按图施工。

阳明心 2023-05-17 11:19 00 [回复]举报

供电局的箱子下面再加个箱不就行了,自己加的箱子里设置消防切电。

关闭

关闭

手机APP下载