消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配水管与配水干管连接

配水干管与配水管连接,应采用沟槽式管件,不应采用机械三通。    这条是不是说明消火栓的立管和平层接时不能采用机械三通?

消防网友18738 | 2021-11-27 22:11
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-11-28 08:00 00 [回复]举报

有关配水干管与配水管的术语是出现在《自喷》规范中。

但配水干管与配水管道连接不能采用机械三通却出现在《消水规》中,有些不妥。目前,消火栓系统,审查与验收还是按此条执行!


龚亮 2021-12-03 08:38 00 [回复]举报

规范是这么规定,不过实际施工中,很多项目都是这么干(开机三),验收时暂时未见验收部门对此点提出整改要求。

关闭

关闭

手机APP下载