消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

公共建筑车库例如办公楼车库是否可以安装燃气管道?

公共建筑车库例如办公楼车库是否可以安装燃气管道?一类高层办公楼内是否可以设置燃气管道,如可以的话应设置在哪里?

同同不同 | 2025-06-22 10:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

重庆消防 2025-06-23 08:59 00 [回复]举报

规范未明确公共建筑车库不能设置燃气管道,但不建议车库安装燃气管道。若确需安装,则需要加强防爆、防火设计。

罗马苏丹 2025-06-23 09:15 00 [回复]举报

没有明确规范,但车库不建议安装燃气管道,太危险了,车库存在易燃物,且电气设备多,通风条件差,人员车辆流动频繁。

一类高层办公楼可以设置燃气管道,建议设置在靠外墙处,万一泄漏了方便扩散到室外;

燃气管道不得穿过卧室、易燃易爆物品仓库、配电间、变电室、电梯井、电缆(井)沟、烟道、进风道和垃圾道等场所;燃气引入管不得敷设在卫生间、易燃或易爆品的仓库、有腐蚀性介质的房间、发电间、配电间、变电室、不使用燃气的空调机房、通风机房、计算机房、电缆沟、暖气沟、烟道和进风道、垃圾道等地方

消防网友68723 2025-06-23 09:50 00 [回复]举报

牛丫头消防课堂 2025-06-23 18:28 00 [回复]举报

第一,高层民用建筑内使用可燃气体燃料时,应采用管道供气。使用可燃气体的房间或部位宜靠外墙设置,并应符合现行国家标准《城镇燃气设计规范》GB 50028的规定。

第二,如果设置,建筑的疏散楼梯间及其前室内不应设置可燃或助燃气体管道。

第三,可燃气体管道严禁穿过防火墙。

第四, 其他防火要求应符合现行国家标准《城镇燃气设计规范》

关闭

关闭

手机APP下载