消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于市政消火栓和室外消火栓动压和静压问题

如果室外消火栓是市政供水,那么消火栓静压按0.14Mpa,动压按0.1Mpa算合格吗

如果室外消火栓设置消防水泵,有消防水池,室外消火栓的静压和动压多少算合格

小胡1983 | 2025-05-20 11:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

空中 2025-05-20 14:50 00 [回复]举报

空中 2025-05-20 14:58 00 [回复]举报

设计工作压力:应不小于 0.6MPa,供水压力应不小于 1.0MPa。  

根据《建筑设计防火规范》(GB 50016—2006)第8.1.3条 为强制性条文,必须严格执行。条文规定:室外消防给水当采用高压或临时高压给水系统时,管道的供水压力应能保证用水总量达到最大且水枪在任何建筑物的最高处时,水枪的充实水柱仍不小于10m;当采用低压给水系统时,室外消火栓栓口处的水压从室外设计地面算起不应小于0.1MPa。


小唐12321 2025-05-20 15:41 00 [回复]举报

看你功能,一般不会设计单独水泵,很多只设计一个取水口,一般室外消火栓是给消防车供水,如果是设计灭火的话,那就需要按照灭火压力了。

牛丫头消防课堂 2025-05-20 22:49 10 [回复]举报

首先,市政管网供水的时候,0.14也不是静压,因为市政管网里面的水自始至终是流动的。市政管网供水的时候呢,最不利点消火栓动压不小于0.1兆帕。

设置室外消火栓泵,动压不小于0.1兆帕为合格,规范没有规定室外消火栓的静压,但如果他用稳压泵稳压,那么静压不小于0.15兆帕。

李勤 2025-05-21 08:18 00 [回复]举报

关闭

关闭

手机APP下载