挡烟垂壁与层高的关系

挡烟垂壁与层高的关系(真诚发问)

小张不迷糊 | 2025-03-20 10:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

潘天坤 2025-03-20 11:02 10 [回复]举报

挡烟垂壁距地可以理解为设计清晰高度,设计清晰高度不应小于最小清晰高度,还有就是要注意挡烟垂壁高度不能低于疏散通道最小净高要求(疏散通道、疏散走道、疏散出口的净高度均不应小于2.1米)


走道、室内空间净高不大于3米的区域,其最小清晰高度不宜小于其净高的1/2

其他区域的最小清晰高度应按下式计算:Hq =1.6 +0.1·H ′  

式中:Hq——最小清晰高度(m);
           H′——对于单层空间,取排烟空间的建筑净高度(m);对于多层空间,取最高疏散楼层的层高(m)。


EHS专家-DL 2025-03-20 11:25 20 [回复]举报

挡烟垂壁高度与层高的关系主要取决于 ‌储烟仓厚度比例‌最小清晰高度‌ 的双重约束。


‌一、储烟仓厚度与层高比例关系‌ ‌

自然排烟系统‌:挡烟垂壁形成的储烟仓厚度应≥建筑空间净高的 ‌20%‌,且 ‌不得小于500mm‌ ‌。 ‌

机械排烟系统‌:储烟仓厚度应≥建筑空间净高的 ‌10%‌,且 ‌不得小于500mm‌ ‌。


二、最小清晰高度对挡烟垂壁高度的限制‌ ‌

定义与计算‌:储烟仓底部距地面高度必须 ‌≥最小清晰高度‌,该高度根据区域类型确定: ‌走道或净高≤3m区域‌:最小清晰高度≥净高的 ‌1/2‌ ‌。‌其他区域‌:按公式计算(Hq=1.6+0.1H’,H’为疏散地面至顶棚高度)‌。‌

层高影响‌:挡烟垂壁高度需满足: ‌层高 = 储烟仓厚度 + 最小清晰高度‌ ‌。 ‌具体计算可参考上面潘同行给出的15K606图集计算方式。 ‌


三、特殊层高场景的处理‌ ‌

低层高建筑(净高≤3m)‌:储烟仓厚度按 ‌500mm‌ 控制(因10%或20%可能不足500mm)‌。最小清晰高度直接取层高的 ‌1/2‌,需确保挡烟垂壁底部高于此值‌。‌

高层或大空间建筑‌:优先采用机械排烟,降低储烟仓厚度需求(仅需层高10%)‌。挡烟垂壁高度仍不得低于500mm,即使层高10%计算值更小‌。 ‌


四、挡烟垂壁高度综合要求‌ ‌

最低限制‌:无论层高如何,挡烟垂壁高度 ‌不得小于500mm‌ ‌。‌

活动式挡烟垂壁‌:需同时满足下垂速度(卷帘式≥0.07m/s)和响应时间(火灾确认后15s内启动,60s内到位)‌的要求。

本安消熊 2025-03-20 16:58 20 [回复]举报

规范来说,只是强调挡烟垂壁高度与空间净高的关系,空间净高一般为层高扣除楼板厚度约0.25m与吊顶及管线空间约0.25m,共需扣除约0.5m。讨论出的室内空间净高+约0.5m(有的吊顶及管线占用更多)才可视为层高。

     对于需要排烟的场所为满足疏散净高应不小于2.1m,同时考虑满足最小清晰高度,则机械排烟室内空间净高H不应小于2.6m,自然排烟室内空间净高H不应小于2.625(对于H不大于3m的场所满足疏散净高便满足了最小清晰高度),故对于室内空间净高H与与挡烟垂壁高度h结合规范要求可以简单归纳表示如下: