消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消火栓立管开机三到底可以吗?

本人在上海干消防,关于消火栓立管开机三这个问题非常头疼,各个区老师验收标准简直不一样,有的老师更本不管这块,有的老师说可以,有的老师不允许,搞的头疼,求哪位大神有合理解释

机会猫 | 2025-03-15 21:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

报告队长 2025-03-17 10:48 10 [回复]举报

 消防给水及消火栓系统技术规范 GB50974-2014  12.3.12-6条 配水干管(立管)与配水管(水平管)连接,应采用沟槽式管件,不应采用机械三通;

EHS专家-DL 2025-03-17 10:57 10 [回复]举报

‌机械三通使用条件‌

允许使用场景:当支管管径≤DN80且开孔直径≤主管直径1/2时,可采用机械三通,但需满足开孔间距≥500mm(机械三通)或≥1000mm(机械四通)‌。

禁止使用场景:开孔直径>主管直径1/2时,必须采用卡箍三通或四通‌。

懒得说 2025-03-17 13:49 10 [回复]举报

如果支管只有一个消火栓,可以采用机械三通


关闭

关闭

手机APP下载