消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

柴油发电机储油间总储量

同一柴油发电机房有两台柴油发电机,储油间分别设0.5立方、0.8立方两个油箱是否符合要求合规,上级专家检查说“柴油发电机房的储油间总储存量大于1m3”是否隐患,那么平时控制储油量使两个储存总量不超过1m3是否符合整改要求?要怎么整改?

chaochaochao | 2025-03-11 10:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

2025-03-11 11:40 00 [回复]举报

设两个储油间,每个不大于1立方

重庆消防 2025-03-11 11:41 00 [回复]举报

建规明确为总储油量,不符合规范要求;通规可以设置两个单间(每个不大于1m3),但未明确总储油量,按你目前储油量,按规范要求设置后,个人觉得可以,可以咨询检查专家。

EHS专家-DL 2025-03-11 11:50 00 [回复]举报

专家所说情况是对的,是隐患。根据《建筑设计防火规范》GB55037-2022和《建筑防火通用规范》中均有提到储油间的总储存量不应超过1立方米。这是针对单个储油间来说的,如果两台柴油发电机可以采用防火墙、甲级防火门分割成两个储油间则合规。您说的平时控制储油量使两个储存总量不超过1m3只能作为日常管理临时措施,从监管角度看存在很大的风险,故不符合整改要求。物理分割才是最佳的整改措施。

潘天坤 2025-03-11 12:36 00 [回复]举报

单间储油间的总储油量要控制不大于1立方米,保证两个油箱实际总储油量符合规范要求也是可以的,可以跟专家沟通看看,实在有争议(可能有人会认为容量超过就有加满的风险)也可以更换其他容量(两个油箱总容量不大于1立方米)的油箱以达到实际储油量不会超过规范要求1立方米的目的


当然楼上专家们提到的按照规范要求将两个油箱分隔成两间储油间也是符合要求的


建筑设计防火规范GB50016正文中描述为:民用建筑总储存量不应大于1立方米

建筑设计防火规范GB50016配套图示18J811-1中的图示描述为:民用建筑每个储油间其总储存量应≤1立方米

由此可推测:建筑设计防火规范GB50016要求的是“民用建筑每个储油间其总储存量”


建筑防火通用规范GB55037中正文提到:建筑内单间储油间的燃油储存量不应大于1立方米

建筑防火通用规范GB55037配套实施指南中提到:因此,本规范主要针对柴油发电机房,也包括用油量较少的小型锅炉房。考虑到有些用途的建筑中设置的柴油发电机组较多且可能比较分散的情形(如电信建筑、数据存储建筑、 大中型计算中心等建筑中的应急发电机房),本规范以一座建筑在同一时间内只发生一次火灾为基础确定了相应的防火基准,因此未严格限制设置在建筑内的储油罐的总储油量,只限制单间储油间内的总储油量


综上所述,个人认为国家技术标准中要求的柴油发电机房中总储油量是指“建筑内单间储油间的燃油储存量不应大于1立方米”,同时油箱容量不能作为作为储油量依据(允许油箱未装满的情况),如果担心加满不符合要求可以更换其他容量(两个油箱总容量不大于1立方米)的油箱,也可以按照规范要求将两个油箱分隔成两间储油间


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准




关闭

关闭

手机APP下载