消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

机械排烟系统 地上部分与地下部分能否共用排烟风机

民用建筑的机械排烟系统,地上与地下可以共用一套排烟系统和风机么?

消防网友59118 | 2025-02-13 18:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

小唐12321 2025-02-14 08:03 00 [回复]举报

没见过

杨杨520 2025-02-14 09:43 00 [回复]举报

防烟系统:当地下部分为汽车库或设备用房时,可共用机械加压送风系统,风量得满足;

排烟系统不建议共用。

消防网友59118   回复: 杨杨5202025-02-15 21:13

竖向机械排烟时是要求了超过一定高度要分段设置,并没有说地上与地下部分一定要分开设置,就算是地下车库也没找到一定要分开独立设置,我的理解是如果是机械排烟的话 满足排烟量就可以了,因为只是着火有烟气的楼层排烟口会联动开启,无所谓地上地下。可现实中遇到的确实有地上部分与地下分开设置的,不是很理解

0    0 [回复]举报

潘天坤 2025-02-14 12:24 00 [回复]举报

同一使用功能的话可以讨论下,不同使用功能的话可能不太合适共用,毕竟汽车库、走道、其他场所排烟量计算方式不太一样

消防网友59118   回复: 潘天坤2025-02-15 21:22

排烟量只是对不同高度有区分 出了中庭 大部分公共建筑层高都没有超过6m,所以并非随机排烟量的问题

0    0 [回复]举报

潘天坤   回复: 消防网友591182025-02-17 08:04

一般来说,汽车库按查表,走道按不大于13000(不管是否高度是多少米),房间按60*建筑面积(其中大于6米的场所按查表或者计算取最大值),三者排烟量是不一样的,如果混用可能不知道如何换算


1    0 [回复]举报

赖峰 2025-02-17 16:16 00 [回复]举报

规范并未禁止,但需要考虑建筑高度和使用具体功能
建筑防烟排烟系统技术标准 GB51251-2017 第4.4.2 建筑高度超过50m的公共建筑和建筑高度超过100m的住宅,其排烟系统应竖向分段独立设置,且公共建筑每段高度不应超过50m,住宅建筑每段高度不应超过100m。

1111111 2025-02-19 09:39 00 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017,4.4.1 当建筑的机械排烟系统沿水平方向布置时,每个防火分区的机械排烟系统应独立设置。

如果水平设置建议。

1111111 2025-02-19 09:39 00 [回复]举报

不建议


关闭

关闭

手机APP下载