消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

自然排烟口距离疏散楼梯间1.5米要求

《建筑防烟排烟系统技术标准》图示15K606第79页要求自然排烟口距离疏散楼梯走道间距大于1.5米,而规范在机械排烟中才有此要求,是否为图示笔误?

SDXDS | 2025-01-20 15:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

徐海金 2025-01-20 16:47 10 [回复]举报

图示自然排烟没有1.5米

潘天坤   回复: 徐海金2025-01-20 17:11

你这个图示内容缺少了


0    0 [回复]举报

徐海金   回复: 潘天坤2025-01-21 08:46

有修订1.5米没有了

0    0 [回复]举报

潘天坤   回复: 徐海金2025-01-21 12:14

确实是把这项描述修正了,是我讲错了,感谢指正

0    0 [回复]举报

潘天坤 2025-01-20 17:14 00 [回复]举报

内容在机械排烟章节,自然排烟是否有这个要求存在一定的争议性,如果有条件建议满足

个人认为图示应该是对机械排烟章节内这个距离安全出口1.5米要求的延伸

业内有些人认为自然排烟和机械排烟均要遵循1.5米要求,当然设置在疏散门上方的情况除外


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准


关闭

关闭

手机APP下载