消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问民用建筑的燃气锅炉房的点型感烟火灾探测器的是否按照防爆设置?

请问民用建筑的燃气锅炉房的点型感烟火灾探测器是否需要设置防爆型的?厨房的燃气表间的点型感烟火灾探测器是否需要设置防爆型的?柴油发电机房的储油间的点型感烟火灾探测器是否需要设置防爆型的?

消防网友69659 | 2024-12-30 11:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

潘天坤 2024-12-30 13:24 00 [回复]举报

燃气锅炉房、燃气表间的用词为燃气,大概为燃气环境,一般需要设置可燃气体探测设施及相关事故通风系统(此风机可能需要采用防爆型)。至于是否为爆炸环境,哪些区域需要设置防爆设施,火灾自动报警系统的探测器是否需要采用防爆型,这个可能还要结合一些条件再深度分析,有存在一定的争议性,有些人认为室内从天花板向下1米以内区域为爆炸危险环境区域,其他区域为非爆炸危险区域


柴油发电机房和储油间的分析,就比较明确了。建规有提到:设置在建筑内的柴油设备,闪点不应低于60°,此环境下的柴油发电机房储油区域应该不属于爆炸环境,从规范来说柴油发电机房的储油间内火灾自动报警系统的探测器可以不采用防爆型。当然设备的选择,可能会参照一些图集或者地方性标准执行,也有一些人认为要考虑“可能发生泄露,需要通过风机排出的情况”,也有些人认为柴油发电机房储油区域属于“建筑内可能散发可燃气体、可燃蒸汽的场所”,这个不过多讨论


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准

关闭

关闭

手机APP下载