气体灭火系统启动方式之一

联动控制器远程启动,这种叫法有问题吗?

消防网友15112 | 2024-12-04 08:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

jinyanwu 2024-12-04 09:38 00 [回复]举报

个人意见,仅供参考:

气体灭火系统分为管网系统和预制系统,管网系统控制方式分为自动控制,手动控制和机械应急控制;预制系统分为自动控制和手动控制;

联动控制器远程启动应该就是自动控制模式

云中飞翔 2024-12-04 12:00 00 [回复]举报

气体灭火系统分为管网系统和预制系统,管网系统控制方式分为自动控制,手动控制和机械应急控制。自动控制由两路探测信号或一路探测信号一路手报发送到气体控制器,气体控制器启动灭火,并将信号反馈至消控室。手动控制是在气体控制器上直接手动按钮启动。机械应急启动实在瓶组间直接手动启动。如果确有必要,也可以实现控制室联控控制(远程手动控制)。

潘天坤 2024-12-04 13:01 00 [回复]举报

个人觉得“联动”和“远程启动”两个名词不适合搭配在一起,规范标准里面好像也没有见到这样的描述

不过如果控制逻辑符合要求,叫法是比较不重要的