消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教一下:消防备电测试问题。

因某些已投入使用的建筑不能断市电,测试双电源时,能否在不断开市电的情况下直接启动发电机供电至末端,再末端进行手动切换测试备电是否接通?或者这种情况下应该如何测试备电?

双电源的规范测试有哪些?哪个规定或有没有相关操作手册

小六951 | 2024-11-12 16:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 12

小唐12321 2024-11-13 09:30 00 [回复]举报

这个不是专业人别去试了,小心炸了

2024-11-13 12:02 10 [回复]举报

不断电情况下启动发电机完全没问题,发电机空载模式启动不产生电流,物业单位运行工每月都空载测试几分钟。

小六951   回复: 2024-11-13 16:47

空载肯定没问题,就是输送到配电柜后,配电柜能不能同时输送两路电到末端双切箱

0    0 [回复]举报

小唐12321   回复: 小六9512024-11-14 08:37

真想测试找图纸,看看能不能一段一段送到水泵房控制柜自动转化开关,然后把市电手动断了,最后在测试启泵看电压稳不稳

0    0 [回复]举报

  回复: 小六9512024-11-15 08:45

物业单位每年对配电房保养一次,保养前会拉闸断开变压器供电,届时可以测试发电机供电情况,市电断开后配电房内的双电源切换开关会自动切换到发电机供电。(配电房保养时发电机切换到手动状态,防止发电机启动)

1    0 [回复]举报

strongcar 2024-11-13 14:17 00 [回复]举报

水泵/风机等大型设备一般是两路市电进双电源控制柜(最末端),自动切换。不会断掉整栋建筑的电。火灾报警系统都是蓄电池做备电,也不会影响建筑供电

小六951   回复: strongcar2024-11-13 16:46

但是从发电机过来配电柜,配电柜无法同时输出两路电吧?

0    0 [回复]举报

strongcar   回复: 小六9512024-11-14 08:36

可以同时输出2路电,但是没必要,发电机不可能一直开着的,只有主电断掉了,信号给到发电机,发电机30秒内启动,切换到备电。当然也可以手动切换到备电

0    0 [回复]举报

小六951   回复: strongcar2024-11-15 09:07

我是说测试时,两路电源同时输到末端,这样可以吗?

0    0 [回复]举报

strongcar   回复: 小六9512024-11-18 08:18

可以2路同时输出到末端,其实你可以把一路市电当成发电机,只不过这个发电机24小时都是开着的。

0    0 [回复]举报

懒得说 2024-11-13 16:52 00 [回复]举报

发电机自动启动本来就不需要切断总电源。火灾区域市电断开信号就可以启动发电机,发电送至末端双电源切换箱后自动切换。

小六951   回复: 懒得说2024-11-15 09:04

备电和市电能同时送到末端双切箱吗

0    0 [回复]举报

关闭

关闭

手机APP下载